loopoyu avatar image
loopoyu asked
Single multiplusII with a 3 phases grid inverter
I would like to install a MultiPlus-II 48V 5000VA on L1 with a SMA Sunny tripower 8.0 grid inverter. The goal is to inject on the grid and to have batteries backup for essential load and night consumption.
Here would be the setup:
- Sunny Tripower 8.0 with L2 and L3 connected directly to the grid.
- MultiplusII connected on L1 between grid and Sunny Tripower.
- Meter ET340
- GX cerbo + screen.
- 300A 48v battery of pylontec 2000c
- MPPT 250/85 with 3000Wc of PV on the battery
- 8000Wc of PV on the Sunny tripower.
1. Will this setup work? whath do you think?
2. Is the factor 1:1 correct?
3. Is the phases imbalance acceptable?
Many thanks
Multiplus-IIgrid3 phasesplit phase
Mike Dorsett avatar image
Mike Dorsett answered ·
Basically the SMA tripower will only operate in a three phase system. So whilst the tripower will work when the grid is present, it will not when the grid fails. you might look at 3 MPII3kW worknig as a three phase set, rather than a single MPII5kW.
loopoyu answered ·
Thanks for the answer