High Current Charging with 2 x Multiplus II in Parallel, ET112 and ESS during Offpeak Rate

Hi,

I'm just about to place an order for 2 x Multiplus II 48v/5000w, 1 x ET112 meter and 1 x Cerbo GX and just need to make sure this is all going to work as planned.

I've been looking through the documentation and forums for several months. From what I've read it looks like it should work but I just wanted to double check / get some assurance that I've not missed something.

I have a cheap overnight rate on Octopus Go, 7.5p/kWh as opposed to 35.05p/kWh during the daytime. We've programmed out Air Source Heat Pump to charge during the cheaper rate and during an excess solar production from the 4kw SMA Sunny Boy.

I want to be able to charge 2 sets of 48v 280Ah LifePo4 Batteries connected in parallel at the terminals only (not between each cell) and managed by a couple of Batrium Cellmate K9's to keep them balanced.

As my cheap rate window is only 4 hours and my safe battery capacity (80%) I'm limited in how many kWh I can put back in the batteries during those 4 hours - 13.44kWh per charger, hence 2 chargers. (2 x 70A)

victronmultiplusiiinparallel-ess-fit.jpg


Will the above setup in ESS mode, allow all the loads in the house to be powered by the Multiplus's and Sunnyboy whilst not exporting anything to the grid, and then charge the batteries back to 90% on the cheap rate electricity ?

or would I be better of with a Quattro 10kw which can charge at 140A native ?

Best regards

Simon.

Multiplus-IIbattery chargingESSmultiplus in paralleloctopus
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
wkirby avatar image
wkirby answered ·

Yes, it will do that. Also it will charge the battery during the day with excess PV power.
If the battery is full and there is still excess PV power then it will be exported.
The trick is to figure out if you will actually need to charge between 0030 and 0430 because there might be enough energy in the battery to see you through to the next day and the next day might have sunny weather. Accurate next day's weather information is extremely difficult to come by.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

simat avatar image simat commented ·

Thanks for the reply, is that the same for the Multiplus II and the Quattro ?

Re the weather - i've been building a house for the past few years, the forecast got me wet many many times. We have polytunnels 200mtrs away, they can signal rain upto 5 minutes in advance.

0 Likes 0 ·
simat avatar image simat simat commented ·
I think the Multiplus II 48v / 10kw is my better choice - also has the 140A charging in a single unit - looks like it costs less than 2 x Multiplus II 48v/5kw
0 Likes 0 ·
Paul Beskeen avatar image Paul Beskeen simat commented ·
Likely too late a response to make a difference - but beware that in the UK that the Multiplus 10kv does not have G99 certification so cannot be grid connected until Victron sort that out - which is likely months away still.