question

dirk-s avatar image
dirk-s asked

Multiplus voltage differences

Hello,

I'm reading in this community for a while now and get many help/hints to setup my storage system. But now I have a questions and didn't find this kind of topic in this community before.

I have just changed my installation from a Multiplus II 3000 GX to a Multiplus II 5000 GX. It is an grid connected ESS System with 5* Pylontech US3000C. Everything works well so far.

But there is one issue that bothers me a bit. The Multiplus have a voltage difference of 0,30 V between the Multiplus itself and monitored in VRM Portal "VE.Bus DC Voltage And Current" and the real voltage. The BMS from Pylontec and all the other voltages monitored and shown by the GX device shows 0,3 higher voltages. I also messured everything with a multimeter and the higher voltages are correct. If I messure also directly with my multimeter on the DC terminal of the Multiplus directly (without calble and inverter/charger are off) the voltage ist 0,3 Volt higher than monitored by the Multiplus.

As the Multiplus uses this messured voltage to steer everything, the real voltage is everytime higher. For example I need to set charge voltage limit to 50,0 Volt to get 50,3 Volt in reality. Also if I don't limit the charge voltage, the real charge limit will be not 52,4, but 52,7.

It may be that these deviations are normal and are the usual variations of measurements. In this case it is ok. But as I still have the possibility to return the Multiplus and to get a new one, I want to be sure. My former Multiplus II 3000 had a deviation of 0,1V.

What are you experiences and values? Are your messured DC voltage by Multiplus the same like messured from BMS/Multimeter/reality or do you have also these kind of deviations?

Many thanks in advance.

Bye Dirk


Multiplus-IIvoltage
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

6 Answers
dirk-s avatar image
dirk-s answered ·

Hi all,

Does nobody from this Community use a Multiplus II 5000 GX who can check this on his/her installation?

Would be very helpfully for me to know.

Thank a lot.

Dirk

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

JohnC avatar image
JohnC answered ·

Hi @Dirk_S

I've an earlier Multi 48/5000 and see a V difference of up to 0.2V. It varies for some reason, maybe a Temperature thing? I 'fixed' it by using DVCC to pass on to it a better V from a Smartshunt.

With your Pylons I don't think you can do that, but the Pylons should be controlling everything anyway if set up correctly. What the Multi reads itself shouldn't really matter. But I've little experience with the Pylons, so check this out for yourself. With managed batts (at least the Victron-supported ones), if they say they're happy, then all should be good.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

anieuwstadt avatar image
anieuwstadt answered ·


Picked up a similar problem. The chart below shows differences between the VE.Bus (MultiPlus) and the BMS (Freedomwon). Conditions: no load, no charging, no solar. The variance is sufficient to put the system into Absorb charge when the BMS battery SoC is being reported as 49%. In the large (6 month) chart, the difference between the voltages is increasing over time. In April at the start of the flat line section, the MP II firmware was updated. Going to confirm the bus voltages using a meter to confirm which is more correct, the BMS or the VE.Bus


1660160936566.png


1660161270221.png


1660161854823.png


1660160936566.png (70.7 KiB)
1660161270221.png (13.4 KiB)
1660161854823.png (110.0 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

cedricr21 avatar image
cedricr21 answered ·

Bonjour, j'ai un problème identique. Mon multiplus II indiqué 51,8v alors que la tension de batterie est de 50v. J'ai mesuré la tension réelle au borne du multiplus elle est de 50v mais le multiplusII indiqué au cerbo 51.8v. Quelqu'un sait-il comment résoudre ce problème ou si je dois l'envoyer en réparation ?

Merci


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Jörg Becker avatar image
Jörg Becker answered ·

Same problem here now.

MP II measures 56,8V when the real voltage over the terminals is only 55.6V. The BMS measures 55.6V, the MPPTs show 55.6V but the Multiplus shows more than 1V more.

Anything I can do about it?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

anieuwstadt avatar image
anieuwstadt answered ·

In my case, there was an inverter hardware issue, and an update to the Venus OS resolved the problem.