In description of this assistant it says when mains is connected on input "This Assistant will be idle when the Multi or Quattro is connected to mains " What exactly is Idle ? - Does mains pass-through ? Does charging follow the settings as per VeConfig3 ? More clarification required


MultiPlus Quattro Inverter ChargerAssistants
1 comment
10 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

This means that it won't do anything until there is no grid, the assistant cannot change the frequency when it has AC-input connected, because it has to follow the frequency of the AC-input.

3 Answers
merle.peter@gmail.com avatar image
merle.peter@gmail.com answered ·

thanks


Share
10 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

merle.peter@gmail.com avatar image
merle.peter@gmail.com answered ·

Interesting :) Where do you get the information thats in the image above from?


5 comments Share
10 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

you have to setup the Assistants as per the settings I have shown you in the picture.

this is off my live system 48/5000 with 4.5Kw of so;lar and a grid Tie 5Kw inverter connected to the AC 1 out of the Multiplus inverter

You are showing ESS and ignore AC assistants, why would @merle.peter@gmail.com have to setup those assistants?

If you want to show the ESS assistant, only show the ESS assistant, but he is asking about the pv-inverter support assistant..not the ESS assistant.

Hi @merle.peter@gmail.com, what exactly are you trying to configure? before we assume all kind of things.

Just trying to under stand the mode "idle" - I cannot find the original reference to it as I think the relevant page has been updated


Boekel avatar image Boekel ♦ merle.peter@gmail.com ·

Ok than my first reply still stands ;)

idle because it cannot do anything with AC-in connected.

Paul B avatar image
Paul B answered ·

This is the assistants that I use on my Grid tie connected inverter, (connected to AC1 out)

my inverter is a multiplus 48/5000

I then use Generator autostart in my CCGX/ venus GX to make AUX1 in the inverter to go hi or low,

Thus this opens the Main AC1 in relay and thus allows the Multi/Quattro to be able to adjust the frequency and thus shut down my grid Tie inverter before the Batteries are 100% full and thus stop export to the Grid.

I use the AC current sensor so that a tile appears on my ccgx/venus gx so I can see the solar current