question

adfilshill avatar image
adfilshill asked

Charging with two independent multiplus

So my client wants to power two cabins with 2 independent multiplus inverters and a shared pylontech lithium bank and single panel array. Each multiplus will have a backup generator. Not sure if charging from genset simultanously is a problem or even if can be set up in Venus. Any sugestions welcome.

MultiPlus Quattro Inverter Chargerbattery chargingVenus GX - VGX
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kevgermany avatar image kevgermany ♦♦ commented ·
Is there grid input as well?
0 Likes 0 ·
adfilshill avatar image adfilshill kevgermany ♦♦ commented ·
No grid
0 Likes 0 ·
2 Answers
Trevor Bird avatar image
Trevor Bird answered ·

it’s not a problem unless the combined combined charge current is higher then the house battery bank can handle. If the battery bank is large it will be fine.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image
Alexandra answered ·

If you want to share a Venus for monitoring the two inverters need to be programmed as a parallel system. And you will need an MK3 to usb for set up and programming.

If you choose to have two separate systems, then DVCC wont work to control the second systems charge, so some care will be needed there (possible warranty void concerns).

And the bank needs to be able to support the full loads of both inverters/be the correct minimum size for two systems.

2 |3000