It's in the manual.. https://www.victronenergy.com/upload/documents/Manual-BMV-700-700H-702-712-EN-NL-FR-DE-ES-SE.pdf Section 4.2.2
The relay itself is specced at
I use the BMV Relays in this manner quite a bit.
As JohnC has pointed out, the relay is only specified at 1A so you would need to have the BMV Relay control a power relay. For DC Circuits, I use a standard 200A 12V relay (you could use a smaller 30/40A relay if the load is small enough), and for AC Circuits, I use SSRs (Solid State Relay), controlling an AC Fridge based on Temp and also an AC Water Heater based on SOC.