My Multiplus-II 48/5000 throws roundabout 3/4 Overload failures a day under normal operation. When looking in my grafana-Dashboard the peak Power-Consumption values does not exceed 4000W. But why does the inverter throws the overload failures and stores them in the cerbo-gx notifiction panel?
My Installation is built up by a Multiplus-II 48/5000 and eight Pylontech US2000 Plus batteries in an offgrid installation.
Multiplus-IIPylontech
grafana or VRM will not accurately see the peaks as the data updates too slowly, around every 5 seconds.
Also the 48/5000 is 5000VA not 5000W. 4000W is around the max sustained load you can put on it.If the ambient temperatures are higher it will be lower.
Thank you, I already thought about that but I didn't remember that it was 5kVA, this would explain the warning messages
marv21 avatar image
marv21 answered ·
Does it shut off? If not, thats not a failure, thats a warning. It warns you it is near to Overload. You can disable this behaviour
8 comments
It does not shut off, its only the warning in the UI
But how can I disable this behavior?
Stop overloading it!?
A short inrush current can also trigger an overload warning but is not visible in UI/log.
JohnC avatar image JohnC ♦ Matthias Lange - DE ♦ ·
@robtor
Matthias is right. It's warning you that something in your system is overloading the Multi. Maybe just a mS spike? invisible to logging.
And it's not adjustable, as it's a hard limit in the Multi. Which can handle it, but it's saying "not for long".
I had this on my 48/5000 regularly, but I knew it was related to a water pressure pump. Replaced the pump start capacitor and problem gone..
Thank you i will check that. But i assume that the error appears wehn the washingmachine and a deep well pump run at the same time.
Maybe I will need to add a second multiplus...
@robtor
That sounds familiar. Mine was a dishwasher heating cycle (2500W with other stuff) plus the (faulty) pump.
I don't recall the GX alarms annoying me, but VRM keeps them forever!!
I didn't actually consider it a serious issue, and never considered upping inverter size. Just Victron telling the full story, not hiding it..
robtor avatar image robtor Matthias Lange - DE ♦ ·
Because of @Marv21 's answer I thougt i could lower the treshold for the notification. But at least the only right solution would be to find the origin of the problem and stop the overloading or adding a second multiplus on the same phase.
I've also recognized that the overloading happens often in episodes of three:
@robtor
The other answers are confusing tbh.
The Overload Warning starts at around 3,5-5kW with the 5KW Unit. There is no caution or something you have to take care of here.
You cant lower (or better rise) the warning trigger here.
You can disable it under your Console. MultiPlus2->AlarmSetup->Overload "Only Alarm".
Ich hab während eines Trainings das auch mal angemeckert, dass es für den Laien echt verwirrend ist eine Warnung abzugeben wenn alles im grünen Bereich ist...
Thank you, I will try that, i've already supposed that this setting could fix the warnings
robtor avatar image
robtor answered ·
@Marv21 Did you mean turning it off by changing the following setting to Alarm only?
Ja genau. Wenn nur Alarm, dann kommen auch nur Alarme wenn dauerhaft eine Überlast war und abgeschaltet wurde.
Ansonsten kommt es ständig.
Russell avatar image
Russell answered ·
I am also having overload problems with a Multiplus ii 48 3000 35. It seems to be linked to loadshedding power dips.
The load is constant at about 150W and a load spike of 900W as the power dips due to our utility switching areas back on (maybe 8:12am). I seem to get spikes of high load which have caused overload shutdown about 3 times this month. This particular spike didn't cause an overload shutdown and didn't affect the PV inverter connected to the grid.
I am still trying to collect more data, using a pc on a ups and a battery backup for the GX device, to see if I can confirm my suspicion. It might also be caused by the borehole pump or other load here on the farm because we are near the end of the utility 11kV power line.
What firmware version is the multi running? Have you updated to the latest?
There was a problem in older firmware versions that would cause the inverter to overload if there were sudden grid changes. Fix now tho.