Victron 100/20 load connection in parallel?

Hi!

Sorry if this is a silly question, but, can I have multiple 100/20 controllers with the load output connected in parallel?


For example, each controller having its own solar panel and battery and having their load outputs combined to achieve for example 1000w?

victron products
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
klim8skeptic avatar image
klim8skeptic answered ·

@Albedo0.39 For example, each controller having its own solar panel and battery and having their load outputs combined to achieve for example 1000w?

This is not a good idea. You will have trouble getting the mppt's to equally share the load current. And the mppt's wont all switch at the same instant, leading to blown fuses on the mppt that switches on first / switching off last.

You are better off using a Battery Protect controlled by the mppt load output to switch the load.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

albedo039 avatar image
albedo039 answered ·

Thanks for the feedback. I did not think of that.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.