Alarm multiplus 12/500/20

Hi.I am electrician in some photovoltaic systems 500 kw and i have the multiplus 12/500/20 with one battery agm 12 v 115 ah.This inverter and the battery is only to supply the high voltage instruments in case of shut down.The problem is that when i have shut down in system power supply (more than 30 minutes) it appears the alarm at the inverter and i must go to the plant to make the hard reset (off and again on).

1)i checked the battery (13.6volt)

2)the only way to reset the alarm button is hard reset??

Thanks a lot

victron products
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Jason - UK avatar image
Jason - UK answered ·

@Georvlac2 What is the load in watts, and what is the DC voltage when off-grid / disconnected from the mains power supply? Are you getting excessive volt drop and / or is the load greater than what the Multiplus can handle?