Victron Phoenix inverter 12/200 circuit breaker?

I have 4 x 12v 100Ah sealed gel batteries in parallel and would like to run a Victron Phoenix inverter 12/1200. I understand they have an internal circuit breaker. Is it necessary to install a circuit breaker between the inverter and battery and what size would be best?

Phoenix Inverter
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
kevgermany avatar image
kevgermany answered ·

Yes, it's needed as close to the batteries as practical.

Better to use a fuse than circuit breaker.

There will be a fuse and cable specification in the manual. But 1200W at 12V is 100A. So you should cable for at least that and fuse accordingly.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

paulshea57 avatar image
paulshea57 answered ·

Thank you kevgermany, that’s exactly what I needed to know!