Not using DVCC nor ESS, how can the DC charging current of a Multiplus be adjusted via Modbus ? Seems like there's no option to accomplish this other than by using VEConfigure or VictronConnect.
Hello
Not using DVCC nor ESS, how can the DC charging current of a Multiplus be adjusted via Modbus ? Seems like there's no option to accomplish this other than by using VEConfigure or VictronConnect.
Why such oversight ? This seems lilke a no-brainer to implement ... Why is it not a writeable modbus register if it can be set through VEConfigure/VictronConnect ?
There is no direct Modbus Register or Access to the Chargecurrent from the Multi or the Mppt's ...
But many many Threads in this Forum about these Problem ...and some (indirect) Solutions ;)
If you enabled DVCC you could set the system charge limit, and it can be changed via node red.
If I set DVCC current, then this influences not only the Multiplus charging current, but also the MPPT current (which I don't want)
If I set to inverter only, then the Multiplus doesn't do passthu.
How can the charging current of the Multiplus only be set without setting the MPPT current as well ?