phoenix inverter 12/500 remote bridge cable size?

Hi, I want to connect a switch to the remote bridge of my phoenix inverter 12/500. Which cable size should I use (distance between inverter and switch approx. 1 meter) ? What is the current flowing trough the bridge?

I cannot find this in the manual.


Phoenix Inverter
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
wkirby avatar image
wkirby answered ·

It's a very low current signal, so 0.5mm² would be just fine as would 22AWG.
If it's too small the jaws of the connector might not grip the copper properly, more of a mechanical problem than an electrical one.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kevgermany avatar image
kevgermany answered ·

I think this is quite an old model. (Just checking I found the correct manual.)

Most of the remote switches are very low current and not particularly affected by wire size. Given the short run I'd be surprised if 0.75mm wire is not sufficient. Ideally put in a wire and measure the current with a meter. It's probably a few milliamps.