amidships avatar image
amidships asked
EasyPlus Compact 12/1600/70 sudden restart during end of battery charging during Absorption
I am running firmware v485, and my EasyPlus is attached to a 200Ah LiFeP04 battery with on board BMS.
I am testing the system in lab before final installation and I noticed this behaviour.
I lightly discharge the battery using the inverter, let's say to 13.09V
The I attach the mains and the charging starts. First the bulk phase kicks in at 50A
Then it soon enter the absorption phase and current decreases:
Suddenly the Inverter and Charger switches off without any warning or errors. It comes back online after few seconds.
It then enter again insto absorption phase where it stays permanently at 98% drawing 0A
I have tried the above with and without AC loads connected but it's alway the same. The EasyPlus kind of "restart" during the current ramp down of the absorption charge and reconnect staying in absorption at 0A and 98% forever.
Any idea?
Thanks!
battery chargingchargerEasyPlus
This can happen if the BMS suddenly cut off the current flow into the battery.
Try to lower the charging current and let the BMS slowly balance the cells.
This should only be necessary at the very first charging.
amidships avatar image amidships commented ·
Thank you very much for the hint. I will try to redo the whole test using 25A as the charging current instead of 50A. But I will still keep 14,4V as absorption voltage as for battery specification (instead of the default 14,2V)
Would you spot any mismatch based om the spec I list here or have good suggestions for a proper charger setup, you are more then welcome to comment.
Thanks!
Specification of battery pack
Electrical Characteristics
Nominal Voltage
12.8V
Nominal Capacity
Minimum: 200Ah
Energy
2560Wh
Internal Resistance
≤30mΩ
Cycle Life
>2000 cycles @1C 100%DOD; >3000 cycles @1C 80%DOD;
Months Self Discharge
<3%
Efficiency of Charge
100% @0.5C
Efficiency of Discharge
96~99% @1C
Standard Charge
Charge Voltage
14.4±0.2V
Charge Mode
CC/CV
Recomm.Charge Current
50A
Max. Charge Current
100A
Charge Cut-off Voltage
14.6V
Standard Discharge
Continuous Current
150A
Max. Pulse Current
500A
Discharge Cut-off Voltage
10V
Environmental
Charge Temperature
0 ℃ to 45 ℃ (32F to 113F) @60±25% Relative Humidity
Discharge Temperature
-20 ℃ to 60 ℃ (-4F to 140F) @60±25% Relative Humidity
Storage Temperature
0 ℃ to 40 ℃ (32F to 104F) @60±25% Relative Humidity
Plastic Case
ABS+PC UL V-0 flame resistant
Dimensions (in./mm.)
L520*W232*H217mm
Weight (lbs./kg.)
27kg
Terminal
M8
Protocol (optional)
Bluetooth
Specification of BMS board
Voltage
Charging voltage
DC:14.4V 3.6V/Cell (CC/CV)
Balance voltage for single cell
3.60±0.05V
Current
Balance current for single cell
116±10mA
Current consumption
≤600μA
Maximal continuous charging current
150A
Maximal continuous Discharging current
150A
Over charge Protection
Over charge detection voltage
3.75±0.05V
Over charge detection delay time
0.5S—2S
Over charge release voltage
3.6±0.1V
Over discharge protection
Over discharge detection voltage
2.2±0.1V
Over discharge detection delay time
10mS—400mS
Over discharge release voltage
2.7±0.1V
Over current protection
Over current detection current
500±50A
Detection delay time
5ms—60ms
Release condition
Cut load,charge release
Short protection
Detection condition
Exterior short circuit
200-800us
Release condition
Resistance
Protection circuitry
≤50mΩ
Temperature
Operating Temperature Range
-40~+85℃
Storage Temperature Range
-40~+125℃
@Matthias Lange - DE , I tried your suggestion of lowering the charging current but the problem still occurs.
Assuming that you are right about the BMS cutting off the current, why should the EasyPlus go in Off and then restart without a warning/alarm? I don't seem to ready about this behaviour in the manual
Chargers.