I have a math problem reading a VRM numbers.
See for yourself.
Total consumption = 1353W
Grid = 20W
From battery = 677W x 0.90 = 609W (90% inv eff)
So VRM math is as follows.
1353 = 20 + 609 ?
Same here.
(this pict was removed to simplify the problem)
Any comments?
Where is the problem?
VRM
Phil Gavin avatar image
Phil Gavin answered ·
Grid CT reversal?
6 comments
marekp avatar image marekp commented ·
There is no CT.
Grid is measured by EM24 power meter in the first pict.
I will remove the second pict because it is confusing the problem because it shows intermittent behavior when inverter/charger is used as grid power meter.
markus avatar image markus ♦♦ marekp commented ·
Hi Marek,
I am pretty sure your EM24 is miswired.
BR
marekp avatar image marekp markus ♦♦ commented ·
There are only 3 input wires and 3 output wires.
How one can miswire this?
Consumer side wired to grid and grid side wired to consumers.
Or phase mismatch.
And EM24 display is up side down.
I thing I would noticed that. :)
Maybe it’s inserted correctly and miswired nevertheless?
marekp avatar image
marekp answered ·
Just to update.
There was a simple reason for the wrong numbers.
Problem was fixed by swapping phases L1 and L3 on the LM24 power meter.
Below the numbers after fixing this problem.
Phil Gavin avatar image Phil Gavin commented ·
Thanks, for the report back, I thought those grid meter readings looked dodgy.
Murray van Graan avatar image
Murray van Graan answered ·
Which batteries are you using? In both instances, the battery discharge rate is roughly half the load?
Winstons (LFP) with "2 signal BMS" in both, but lets concentrate on the top one only.