goboating avatar image
goboating asked
Victron Autotransformer wiring options
Boat currently has 120 30amp service
needs 220v for new ac
1 option ( I’m told) is to pull 120v from a breaker on main panel
to the victron autotransformer and the 220v out to the ac unit
2 option
ac out 1 from Quattro to autotransformer wired to 120/120/220
split then 120 to A side of current panel 120 to B side and the 220 to a sub panel with breaker for the ac unit.
is one way better than the other.?
im concerned about option 1 because I can’t find anything like that described in any victron manual
Autotransformer
wkirby avatar image
wkirby answered ·
Option 1 would look like this:
That image is taken from the datasheet here:
https://www.victronenergy.com/upload/documents/Datasheet-Autotransformer-32A-and-100A-EN.pdf
Instead of the source being an Inverter / Charger as depicted, it would be the breaker in your panel. Does that help you?
goboating answered ·
Ok, but if I do it option 1
what about ground relay in the inverter?
it says it needs to be used?
Harold Lopez avatar image
Harold Lopez answered ·
I am having a similar issue. I am trying to figure it out right now, but i am using this diagram. AT-1-split-phase-240V-to-120-240V-with-Quattro-240V.pdf