Victron multiplus 12/1200/50 Relay activation

Hi,

Trying to get to use the multiplus relay to activate when AC is cut off, but cant seem to get it to work. It is set up like this:capture.png

When i measure between COM and NC/NO nothing happens when I disconnect AC power. What I am doing wrong?

Regards

Baard


MultiPlus Quattro Inverter Chargerrelay assistant
capture.png (9.3 KiB)
2 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

Do you also have a assistant to switch the relay to ON?
(You can't switch it OFF if it wasn't ON :) )

1 comment
2 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

That did the trick! Thank you very much! Quite logical, but did not think of it that way :-)

netrange avatar image
netrange answered ·

Die you send the changes to your System ?