Topper avatar image
Topper asked
Phoenix Multiplus 24/3000 sinewave starts clipping at half load
I have a Phoenix Multiplus 24/3000/70 old model and when it's turned on and there is no load on the output the sinewave has a nice curve see next photo;
But when i put a load of 1600W on the output the sinewave starts clipping, see next photo;
Is this normal for a older version of this Phoenix Multiplus or is there something else wrong?
Thanks in advantage for any reaction.
MultiPlus Quattro Inverter ChargerPhoenix Inverter
5 comments
What kind of load? What about the battery voltage at this moment?
Topper avatar image Topper Matthias Lange - DE ♦ commented ·
@Matthias Lange - DE The load is a water cooker, with no load the battery voltage is 24,0V with the cooker on the battery voltage is 22,4V
wkirby avatar image wkirby ♦♦ Topper commented ·
That no load Voltage is pretty low to start with. 22.4V is also really low, no surprise it is clipping.
You have ~70A load on the battery, what size is the battery?
Topper avatar image Topper wkirby ♦♦ commented ·
@WKirby the battery’s are 2 Victron gel 12V / 220Ah deep cycle in series. The no load voltage looks to me ok if its 24 Volts
Paul B avatar image Paul B Topper commented ·
A full LA battery should be around 25.4 at NO load depending on Temp to some degree as well, see if graph below helps.