t-energy avatar image
t-energy asked
Solar feed to AC Out-1 + AC Out-2 on a Quattro ?
Hey! Please advise, it is possible:
  • We have a stable input 230V 100A (sometimes there are blackouts)
  • We want to supply Quattro 48/10000 and connect PV ≤9kW via controller MPPT 250*100 *2 pcs
  • The battery will always be charged.
  • Maximum load on AC output-1 ≤ 7kW
  • Maximum load on AC output-2 ≤ 10kW (when the input network is available)
Q1: Will solar energy be shared between AC Out #1 and AC Out #2?
Q2: If the consumption is small during large PV generation, is it possible to set up a power discharge to the grid?
Q3: Do I understand correctly that when AC Input #1 disappears, AC Out #2 will automatically turn off?
Thank!
MultiPlus Quattro Inverter ChargerESSsolargrid
Warwick Bruce Chapman avatar image
Warwick Bruce Chapman answered ·
Note, I assume 9kW of PV and not 9000kW.
Q1. Yes.
Q2. Yes, enable "Feed in excess DC" in the ESS menu
Q3. Yes, that is the default behaviour.
t-energy avatar image t-energy commented ·
Thank you so much!
p.s. fixed mistake PV power.