Possible Bug in VE.Can MPPT - High Battery Voltage Alarm

I had many High Battery Voltage Alarms after install today of the first 250/100 VE.Can

Good news is we now have another 3,920w Solar array working on the boat!

But the alarms were triggered by the MPPT relay output set at 28.00v and off at 27.90v. (I was hoping to use it to turn on a battery fan during charging)

Every time the MPPT hit 28v the alarm was triggered and cleared below 27.9v, but I didn't expect an alarm warning from setting the relay. (Simple FLA battery bank 28.90v Abs, so alarms were below Abs voltage)

Turning off the relay didn't stop the alarms, but setting the Voltage trigger points of the relay higher have at least stopped alarms for now.

Setting a disable alarm rule in VRM also didn't stop the alarms.

Smartsolar MPPT VE.Can 250/100 v3.04

CCGX V2.63

These Settings stopped the alarms (Setting the relay to be triggered at a higher voltage than battery voltage):

mppt-vecan-relay-settings.png

VRM Rule that didn't stop the alarms:

alarm-rule.jpg

Alarm Logs:

alarm-logs.jpg

MPPT - Solar Charge ControllerVE.Canmods
alarm-rule.jpg (69.2 KiB)
alarm-logs.jpg (174.6 KiB)
1 comment
2 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Hi Al, thanks - I’ll make sure we double check on our end

2 Answers
mvader (Victron Energy) avatar image
mvader (Victron Energy) answered ·

Hi Al, second update - its been fixed. Released today as v3.05. Item from the change log:


  • Fix triggering “Low/high battery voltage” alarms on the GX Device, if connected over VE.Can, when the charger’s relay mode is at “Battery voltage low” or “Battery voltage high” with the relay active. The alarms are not triggered when connected over VE.Direct. Now the alarms are never triggered on the GX Device, regardless of which interface is being used, when the relay condition is met.


Thank you again for pointing this issue out.

2 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mvader (Victron Energy) avatar image
mvader (Victron Energy) answered ·

Hi Al, I checked, and indeed this is how it works now.

the relay settings also affect alarm indicators.

We’ll work on a solution, I dont know if this will take long or short.

3 comments
2 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Thanks for the update. I'm using Quattro relays instead, but I'll keep an eye on the updates and changelog.


Hi Al, update: this will take a few weeks maximum.

the fix will be that the mppt no longer creates these high (and low) voltage alarms.

Right now it does, but only on VE.Can. And it shouldn’t do that, since they are not configurable.

Al avatar image Al mvader (Victron Energy) ♦♦ ·

That's good to hear, thanks.

Yes, it seemed strange when setting the relay to trigger on high low voltage it would also trigger an alarm at the relay setpoints.

I didn't test if any of the other relay settings in use triggered the alarm also, but assume if this fixes the creation of the High Low Voltage alarms then it should be the safe to use the other relay triggers without alarms in future.