question

louie-astorga avatar image
louie-astorga asked

What is “#3 Expected Devices Error”

On a split-phase multiple 12/3000/120 I get an “#3 Expected Devices Error” followed by a “low battery error on the Color GX panel when removing from the 50amp RV park service and the slave goes off-line. Batteries SoC shows 99%. All works well when plugged in. No errors or notifications.

error
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Paul B avatar image Paul B commented ·

so what happens when you turn both off and back on via there rocker switchs does all then work fine, ?????


also if they do work fine then with the CCGX what happens if you go to the list select multiplus and turn them off, wait 3 min does a error occur, then if you turn it back on they all work fine. I only ask this question out of interest. (a error should not show)


0 Likes 0 ·
louie-astorga avatar image louie-astorga Paul B commented ·

Will try that.....

0 Likes 0 ·
0 Answers

Related Resources

Additional resources still need to be added for this topic