According to the Victron guide the minimum nr of PylonTech US2000s is 7 on a Quattro 48/10000. What would be the minimum needed for PylonTech US3000s ??? THX!!!!
All the info required to calculate the number of modules is in the above, yes its less than specified in the victron table for the larger modules. Do some maths and feel free to ask if your are correct.
@pabloc39 5 US3000 batteries is the minimum requirement for the Quattro 1000.
The continuous power rating of the battery bank must exceed the maximum continuous output power of the Quattro - 8000W. Five US3000 batteries are rated at 8880W continuous @48Vdc.
Don't forget to use two sets of battery cables to connect the pylontechs to your Quattro, i.e. two positives and two negatives. One set is rated at 120A, which your inverter will exceed when pulling more than 5760W @48V off the batteries.
23 People are following this question.