My trailer has an Onan gen with split phase (120V each) and each feeds half of the AC distribution. I intend to set up the trailer with solar and lithium Iron Phosphate batteries. My question: Is it possible, when the genny is needed for loads and charging, to run each of the phases through their own Multiplus in pass through to power the AC as originally configured in the trailer? And I was thinking each Multiplus would ideally need its own battery bank. Am I totally out to lunch with this way of thinking? I have searched the internet with not much luck. Thanks.
split phase
Pat Davitt avatar image
Pat Davitt answered ·
Maybe. I assume you have 2Kw or 3Kw 120V Multipluses. The Datasheet says you can"stack" two inverters one on each hot leg and provide a 120/240V split phase output. What I cannot find anywhere is confirmation of how well a 120/240V split phase source (Your generator) will perform with pass-through and charging in this stacked arrangement.
I live in the US so I have a great interest in getting a definitive answer.
Pat
natebert avatar image
natebert answered ·
In our system, we run two Quattro 12/5000/220-100/100 120V Inverter/Chargers for normally operating on a 50a RV service (240 split phase I believe it's often called). We wired leg 1 to the first inverter, and leg 2 to the second inverter. We then wired the output of each inverter to each 120v leg of our RV.
When on a normal 50a grid service, each inverter/charger operates normally. When on a 30a single phase 120v, split over the 2 legs (both legs on same phase) the first inverter operates normally, and the 2nd inverter rejects the signal and goes into inverter mode drawing from the batteries to make up the other (out of phase) leg. (effectively still maintaining the other phase in its output).
So when adding a 120v generator, when used with an upstream transfer switch, the grid load comes from the 5500w Onan as the same phase (on each leg) and effectively becomes the same thing. The first inverter takes the signal from the generator, the second inverter rejects it and creates its own out of phase leg from the batteries. The first inverter then charges the batteries to make up for the draw from the second inverter.
Its not a perfect solution, but you can read about others with similar experiences here.
https://community.victronenergy.com/questions/122/multiplus-inverters-setup-in-split-phase-to-match.html
In an effort to work around this, we recently commissioned a transformer to be hand-built which should convert the two 120v legs of the Onan into split phase 240 (including creating a new neutral to handle the full load) to feed into the two Quattros allowing them full pass-through operation without having to invert 1 leg. (I've read that the Victron Autoformer would not work very well in this situation due to the amount of potential imbalance of the two legs.)
Their maybe other ways around this and additional discussion can be found in that other thread.
You may also want to check to see if your Onan really offers a true 120v split phase, or if it's simply the same phase split across 2 circuit breakers (as was the case on our unit.)
Good luck and I'm eager to see what others offer as possible solutions here.
Nate
ben avatar image ben ♦ commented ·
Great answer, and I have a few comments:
1) “Autoformers” and “autotransformers” are two different things, frustratingly enough. The relevant component — and the one Victron makes and sells — is the latter, an autotransformer.
2) The big Victron autotransformer can sink 32A of current on its neutral, which means you can have an imbalance of up to 120V * 32A = 3800W on the two legs. Or, seen from the other direction, you could step up 3800W of 120V to 240V, give or take a little from the conversion losses.
colin59 avatar image colin59 commented ·
I am in process of installing a similar system in my motorhome, I have a 7500 Quiet Onan wired 2 legs same phase 120V through a 2 pole 35 A breaker with 2 neutrals 2 hot and 1 ground. I would be interested in your inverter, how you are wiring it, results and if it would be available to others. Is there a specific reason you didn't use the Victron or Outback Auto transformer? I looked at those and was wondering if I could just wire one leg through it and connect only the transformers 180 degree out phase output to my second quattro... This would put 0 load on the other outlet so would limit current 20 about 30A ok for my generator output.
ben avatar image
ben answered ·
Yes, this is the standard meaning of two “stacked” inverters in split-phase in a North American configuration.
As long as your generator is a 240V generator (that’s what two 120V hots at 180deg phase angle really are), you can do this.
You can also connect them both to the same battery bank. No need to split it up.
When you connect to a shore 120V supply, you will see the “divided” operation that Nate describes in his excellent answer: one will charge/invert/pass-thru like normal, and the other inverter will switch to invert-only off the battery. In practice this doesn’t really change anything and the system will work just like you’d want it to.
You might check with Onan and see if they have a conversion kit to change the 120V output to 120/240 Split Phase. I have a Generac 6KVA generator at my house and they had such a kit. It depends on the generator windings whether this is possible or not.
In my case all I had to do was re-route a few wires and change out the single circuit breaker for a ganged two circuit one. Took about an hour.
Pat
natebert avatar image natebert commented ·
Hey Pat, Great suggestion and I looked into this, but supposedly the windings inside the genset are fixed to the same phase, effectively requiring a purchase of their upgraded model of 'commercial' line or similar generators, in order to get 120v/240v.