Koul Alim avatar image
Why aren't my Quattro 48/15000 switching when there is an AC source at the ACin 1 in input, in the 3-phase configuration?
I have 3 Quattro 48/15000 configured in a 3-phase system.
When ACin is connected, the system doesn't switch and stays in inverter mode. Through VEConfig 3 / CCGX, here are the parameters read.
Why is Current = 0 A?
In stand-alone mode, each unit switches properly.
ACin parameters
Frequency = 50 Hz
Voltage = 230 V
MultiPlus Quattro Inverter Charger3 phase
Hi @Koul Alim
on your last photo (stand alone) I see 187V input voltage...I think there is something wrong with your grid input.
first check: a neutral disconnect somewhere, causing the phases to float...and potentially putting 400 VAC on one phase (and you don't want that..)
on phase rotation: with your firmware version you should get a message in the Multi-menu in the console, but also you can just try to swap two phases and see if that works.
Hi @Koul Alim
see the answer from Matthias.
also, what firmware are you running?
Hi @Daniël Boekel. The current firmware running in the units is 2656476
Do you have a GX device?
Maybe you have a wrong phase rotation at the input?!
Yes. there is a CCGX.
How can I make sure it is due to wrong phase rotation?