VE.Bus System [261] on VRM

can anyone shed some light on this error? seems to only happen in the twilight around 7pm and dusk at 5:30am

multi-plus 2 , byd b-box 5kw , MPPT 150/70 , Fronius 3kw in parallel with grid meter

MPPT - Solar Charge ControllerMultiplus-IIBYDFronius
4 comments
10 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Harvey_ricky avatar image Harvey_ricky mvader (Victron Energy) ♦♦ ·

I have tried to look for the error code ,I assume that's what the number beside it means?

screenshot-11.png (246.5 KiB)

261 is not an error code, it is the Device Instance or Device ID if you like.

You need to check what alarm rules you have set up which are generating these alarms.
Go Setting -> Alarm Rules to see what you have set up for your site.

thank you that will save a lot of unnecessary emails.

but why the warning?

2 Answers
WKirby avatar image

Without us being able to see your alarm rules, we cannot say.
It depends upon what the alarm is pertaining to. Eg. Temperature is one of the ones that has "Alarm", "Warning" and "OK" levels.

Share
10 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Guy Stewart (Victron Community Manager) avatar image

The warning was a low battery warning.

But it seems to be a mistake, I can't see anything that would have triggered it, battery voltages, loads and states of charge are all normal and consistent before, during and after.

It had no impact on the system, and corrected itself.

Was there a local alarm on the CCGX?