EasyPlus Compact 12/1600/70 - Fuse Size

Hi All

Can someone confirm the correct fuse size to use ? I am thinking of using a 150A fuse.

My logic is -

When charging - the max it could throw to the batteries is 70A. When inverting the max it could be pulling from the batteries is 1600W / 12v = 133A plus about 10% = 150A.

So a 150A fuse would cover charging and inverting.

Thoughts ?

Thanks

Tim

fusesEasyPlus
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
JohnC avatar image
JohnC answered ยท

Hi @Miya

The actual rated max output for that unit is 3000W. But that won't be for long before it trips, and it's really just to handle load spikes. If you're using the supplied 35mm2 cables, you could safely run a 200A slow-blow fuse.


3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

miya avatar image miya commented ยท

Hey JohnC - many thanks - that's great - I will go with that.

0 Likes 0 ยท
amidships avatar image amidships commented ยท

Hi @JohnC

I was wondering, the 35mm2 cables provided with the easyplus are rated to 60ยบ

Would a fuse of 150A be a better safer choice? Given that the max continuos output from the EasyPlus is 133 A?

See table below

https://www.bluesea.com/resources/529/AllowableAmperageinConductors-WireSizing_Chart


@Miya, what fuse did you end up using?

Cheers!

0 Likes 0 ยท
klim8skeptic avatar image klim8skeptic โ™ฆ amidships commented ยท

I used an 160a NH00 fuse.

Seems to withstand an overload of 200a. Microwave running, and fridge kicks in. Std compact wire, approx. 1m.


multi-12-1600-70-peak-current-draw.png



0 Likes 0 ยท