filipmartin avatar image
filipmartin asked
transfer switch from Victron trips RCD when changing between power sources while under load.
I have a transfer switch from Victron. It is used to switch between solar power & grid power.
When a switchover happens, e.g. from solar to grid, while there is a heavy load (>2000W) sometimes the grid RCD trips.
I think the RCD trips when an arc occurs inside the B&J R40-22 relay of the transfer switch.
What can I buy from Victron to fix the problem?
FYI, not clear to me why Victron is using a relay instead of a dual contactor with mechanical interlock to do the switchover?
The switchover would be a bit longer than 20msec but for sure no arc can occur between the 2 power sources that may trip an RCD (type A , B, ..)
type of switch : https://stroomwinkel.nl/ve-transfer-switch-5kva-230v.html?gclid=CjwKCAiA4OvhBRAjEiwAU2FoJaKZYx0k2MUZe1HeVRckhrjAxANvnRpu6nRt7NruNR0X5wXTn8mfpRoC6DIQAvD_BwE
Thanks in advance for your response.
Regards,
Filip
switch
filipmartin answered ·
Maybe i should ask this question to someone from Victron itself.
Does anyone know how to contact them?
Regards,
Filip
Hi Filip; the point of contact is your dealer; they are trained by us to give support to end users and installers.
De stroom winkel is very knowledgeble; you are in good hands there.
See also here for how to get (pre or after purchase- ) support:
https://www.victronenergy.com/support
Thanks MVADER, but so far nobody has been able to answer me.
To anyone interested, i can confirm that the relay is the cause of the issues. I have replaced the Victron transfer switch and the problem is now fixed. A relay with 2NO & 2NC contacts is not really suited as a changeover switch which is under load.
If anyone from Victron is listening, i would still like to hear how they would handle this issue. I assume this is a known issue for which they probably have a workaround. Maybe by adding arc suppressors.
Regards,
Filip