Spyros Tziakouris avatar image
Spyros Tziakouris asked
2 Smart Battery Protect 48V - 100A low voltage output
A 48v system, has 4 victron lifepo4 12,8V 300Ah, 2 Battery Protect 48/100A. BP1 has the 48V loads connected. BP2 has one non-victron Inverter connected, 2.3kVA. BP48-100.jpg
Issue: While Battery Protect 1 is working fine, MCB of the second load is switched on. On that moment, BP2 is activated. BP1 seems to work fine, but voltage output is only around 5-10V. to fix this, MCB for BP 1 is switched off and on again.
Both BP get signal from VE.bus BMS. is this due to the surge current from inverter? Can we use BP with inverters rated below 2.5 kVA?
Regards,
Spyros
BMSBattery Protect
To cut off the inverter you should use a cyrix-li-load instead of the BP.
Justin Cook avatar image
Justin Cook answered ·
@spyrostz, using the BP to directly disconnect the main DC line of an inverter (any inverter) is expressly forbidden. The only approved method of using a BP to trigger an inverter on/off is by using it as a trigger for the remote on/off of an inverter (if so equipped - Victrons have a remote on/off but you mention it's a non-Victron, so I don't know if you have one or not).
Please see the recently updated BatteryProtect user manual, which has several sample diagrams showing approved connections.