If your generator is running on auto-start and is manually shut down, will this create a error code (red light). Looks like the fix is to disable and then enable the auto-start again?
Yes, you must turn off Auto Start to stop the generator from the GX device. If you stop the generator external to the GX device then the GX device believes the generator is still running. If you connect the generator run to a digital input programmed as Generator then you will get an alert if it is enabled in generator start/stop menu.
GuiMods includes some generator enhancements in this area:
Run time accumulation factors in the state of the Generator digital input: if it's false, then time will not accumulate.
The GX device's manual run state is synchronized by changes in the Generator digital input so that if the generator is shut down externally, the GX device will cancel a manual run. For auto runs, a warning is shown on the Generator Overview page but does not cancel an auto run.
I am having a similar issue. When my generator starts on automatic and I want to discontinue the Run I manually turn it off after placing the auto start in off. When I restore the auto start immediately after the generator has been shut down it restarts. Apparently if the auto start does not see the shutdown parameters it restarts the generator. I have a digital input telling the GX unit that the generator is running.
Note that in GuiMods, I've added a way to manually start the generator before the automatic start thresholds have not been met and let the automatic stop logic stop the generator. This is the opposite of what you are asking for.
The question becomes: when should the automatic logic take back over after the generator is manually stopped?
I agree with you and I'll just provide some further clarification. My auto start functions are set for only two parameters. Battery load of 70 amps or more for 100 seconds and SOC of lower than 63% and will shut off at 80%. If the generator starts on SOC and runs to 70% and I turn it off manually, when I place it back into Auto the generator restarts even if the state of charge is over the trigger threshold of 63%. It's a simple work around to leave it manual until the batteries have been recharged by another source however necessity being the mother of invention I believe laziness is the father and I prefer to be lazy LOL
I made some changes in the autostart logic as part of GuiMods v10.48.
Now, if the start conditions are all satisfied when autostart is enabled, the generator will NOT start.
So now you can turn off autostart to stop the generator manually and it will not restart. Of course it will start if at least one start condition is active.
For example if the SOC start threshold is 30% and the battery HAD reached that level but is now at 50%, turning off autostart, then back on again (after generator is stopped), the generator will remain stopped until the threshold drops below 30% again.
Cerbo GX - Generator auto start/stop
Automatic Generator Start/ Stop [PDF]
Automatic Generator Start/ Stop [Online]
42 People are following this question.