guenserge avatar image
guenserge asked
feed-in power displayed on CCGX seems wrong?
Hello Guys,
I hope you are doing fine. I have some issues with my installation. I have a 3-phase backup system of quattros and a solar inverter connected at the output of the quattros. AC input of quattros is connected to the grid and feed-in is allowed.
Please have a look at these two pictures
Here AC-in power = - 4761 W
But in the menu, AC-in power = - 2324 W
Why the two values are very different? -4761 W is more than the double of - 2324! And I thing -2324 is the correct value as solar production is 2580W and power going into batteries is 216W, then the surplus feed-in energy must be around 2580 - 216 - power loss in quattro.
Thanks for your answer.
CCGX Color Controlgridsolar
Hi @guenserge
The PV inverter is probably configured as connected on ac-in, while it is actually on the output, I think that's why it is counted double.
Hi @guenserge,
Does your system have an energy meter?
I would check the wiring of it to make sure that it is correct. Some photos with a system wiring diagram would help with diagnosis.
4 comments
guenserge avatar image guenserge commented ·
Hi Guy Steward,
The system doesn't have energy meter, I used SMA Tripower STP 7000 TL with webconnect interface directly connected to the CCGX.
Guy Stewart (Victron Community Manager) avatar image Guy Stewart (Victron Community Manager) ♦♦ guenserge commented ·
Ok, next thing to confirm is the settings of the AC Solar PV Inverter support and ESS assistant from VEConfigure. As described in the AC-Coupling manual.
Could you please post a screenshot of those configuration settings?
guenserge avatar image guenserge Guy Stewart (Victron Community Manager) ♦♦ commented ·
I used PV inverter assistant instead of ESS assistant. below is my configuration:
To help isolate the cause, does the doubling disappear if you disconnect the SMA comms cable?
Also, can you please post a system wiring diagram.
guenserge answered ·
Hello Guy,
The site is very far from me. Kindly find attached the diagram of the system
@guenserge
Did you read my post?
This you can easily set through VRM.
guenserge avatar image guenserge Daniël Boekel (Victron Energy Staff) ♦♦ commented ·
Hello Daniel thank you for your reply, I'll find how to change it through VRM and will let you know if it's ok. thanks
I just made the change on VRM and everything seems to work perfectly now.
Thank you for your Help Guys, I'm very satisfied.