Is it allowed to connect a Fronius Primo 3.6-1 to one ACout1 from one of the 3 MP2?
Or is it just recommended to connect a 3 phase Fronius to a 3 Phase ESS?
Is it allowed to connect a Fronius Primo 3.6-1 to one ACout1 from one of the 3 MP2?
Or is it just recommended to connect a 3 phase Fronius to a 3 Phase ESS?
As long as you are within the factor 1.0 rule it's totally fine.
https://www.victronenergy.com/live/ac_coupling:start#the_factor_10_rule