manta avatar image
manta asked
Victron 3-phase multiplus II AC wiring
I am setting up 3 Multiplus II 48/5000/50 in a 3 phase configuration in combination with 4 batterypacks (on Lynx distributor & lynx power in) of 15kwh each.
So far its great, i have a 5x 4mm2 comming from the 3 phase grid (4 pole 25A breaker), As i can see i need to split this in three neutrals. One to every multiplus.
I think there is going to be a lot of current flowing trougt the connected neutral, all tree multiplusses are going to be connected to the same nautral. So i would need to make a small case to split the three phases, what is the right way to do this. Just a 4-pole switch and a distribution block for the neutral? Or is it better to use 3x 20A 2-pole breakers / switches?
Anyway can anybody inform me what is the normal way of distributing the power to the multiplusses?
3 phase
Alexandra avatar image
Alexandra answered ·
@Manta
You need to talk to an electrician.
You should never interrupt the neutral on a three phase system. And it should be common.
There will be current on the neutral if you have unbalanced loads.