bradleyasmith avatar image
bradleyasmith asked
Victron 200ah smart battery cable run size
Do cable runs between each of four Victron 200ah smart batteries and a Lynx Distributor #1 (on left side of Lynx BMS) require 4/0 cable? Or would 2/0 be sufficient? I will be using 4/0 cable between the 3000 Multiplus II inverter/charger and the Lynx Distributor #2 on the right side of the Lynx BMS.
Lithium Battery
kevgermany avatar image
kevgermany answered ·
Size for current. As we have no idea of loads, we can't answer the question.
bradleyasmith avatar image bradleyasmith commented ·
Max current draw of 225 amps, for short period. Usually much less.
Refrigerator 1.5 amp
Fan 2 amp
Lights 1.5 amp
Water pump 7.5 amp
12V AC 58 amp
Cooktop 140 amp
Microwave 80 amp
kevgermany avatar image kevgermany ♦♦ bradleyasmith commented ·
You can split the total load by 4 between the batteries.
Best cable for theoretical max.
Maybe AWG 3 or 2 to the lynx.
bradleyasmith avatar image bradleyasmith kevgermany ♦♦ commented ·
Thanks!