Multi RS & Lynx Shunt with different SOC

Hi,

I recently upgraded my system with a Lynx Shunt and now the Multi RS shows his own SOC (few % more). I have a 10% dischage limit, but today the Lynx Shunt showed 6% but the Multi RS (SOC 11%) didn't turned off. Before the upgrade the Multi RS used the Smart Shunt's SOC.

System before upgrade:

Multi RS Solar 450/80

Smart Shunt

MPPT 150/45

MPPT 100/20

2x 14kW Lifepo4 Battery

Cerbo GX

System after upgrade:

Multi RS Solar 450/80

Lynx Shunt + Lynx Power In

MPPT 150/45

MPPT 100/20

2x 14kW Lifepo4 Battery

Cerbo GX


I can chose in the Cerbo system setup -> Battery monitor which SOC should the system use. After a complete reboot it has no effect. I can't use the Multi RS SOC because I have two more MPPTs.


What could be the problem? Do you have any suggestions? Is the Multi RS compatible with the Lynx Shunt?


Thank you.

SOClynx shuntMulti RS
4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Hi @UBI,

Thanks for the report, I'll see what I can find out.

1 Like 1 ·
ubi avatar image ubi Guy Stewart (Victron Community Manager) ♦♦ commented ·

Another interesting fact: When I use the BMS as the "Battery monitor" in the Cerbo system setup, the Multi RS uses it immediately. It only doesn't work with the Lynx shunt.

0 Likes 0 ·
Hi @UBI

Indeed there appears to be a specific limitation with the Lynx Shunt and RS inverters.

The engineers are now aware and I’ve just asked them for an update on the situation.

0 Likes 0 ·
semlohnhoj avatar image semlohnhoj Guy Stewart (Victron Community Manager) ♦♦ commented ·
I use a lynx shunt and two Multi RS Solar units and all three show different SOC values
0 Likes 0 ·
1 Answer
Martin (Victron Energy) avatar image
Martin (Victron Energy) answered ·

We just released firmware v1.10 for the Lynx Shunt VE.Can which addresses this issue. It it available on Victron Professional and through the VRM firmware update feature.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

semlohnhoj avatar image semlohnhoj commented ·
I had to reset the SOC after installing the firmware update but I can confirm that the update has resolved the issue for me. Both of my Multi RS Solar units now show the same SOC as the shunt.
2 Likes 2 ·