I had a set of 330 ampere/hour batteries running on my MultiPlus 48v. I added another set of batteries in parallel, made changes to the firmware to 660A/H, but the output power did not increase. What could be the reason? Thank you.
What inverter? What is the amps out of the battery? capacity (storage size) is not relavent to power out, but the ability of the bms is.
What do you mean by the statement the power output has not increased? All you have done is added capacity to storage not increased power.
Thank you for the quick response @Alexandra
Equipment:
3* inverters MultiPlus-II 48v 5000VA
8* Lithium Battery Smart 330Ah 12,8V (4 and 4) 330Ah 48v + 330Ah 48v. Total 660 Ah
Lynx Smart BMS 1000A
I mean the battery capacity has not increased, I get 9-12 kW/hour when discharging, but I should get more than 20 kW/hour
What settings need to be made if one section of the battery was working, and I added a second section in parallel and increased the capacity.
Тhank you.
Confirm none of the batteries have any communication with the GX?
If you are running ESS, then you might find it is using the dynamic cut off voltage set there for the load running at the time of shutdown.
I use Cerbo GX to control the system. But the batteries are connected to the BMS.
In the VRM portal, I do not see parameters that limit the capacity delivered by the batteries.
Perhaps you can look at my configuration file or give recommendations on how to add battery capacity to the system. Thank you.
Good afternoon, @Alexandra .
I still don't have any extra capacity from the second battery section. Please tell me what settings need to be made in the system when installing an additional set of batteries.
Thank you.
If you do lower all the cut off voltages in the assistant to the low cut off for the bank.
How are they wired? Do they have good current sharing?
Are any if them shutting down before the others?
57 People are following this question.