I installed 36 pannels in 4 strings all same orientation and no shading. The 450|200tr has 4 imputs No.4 has allways a lower yield. In low light this is particularly noticeable. I have swopped the strings around to see if the problem was in the pannels but No.4 imput is allways down on performance. I set up the system 103 days ago with just 24 pannels so I wasn't using Imput No.4 then I completed the arrays 51 days ago and I've been hoping the problem will go away but no joy.
These are the figures for today:
No.1 8.3kwh, 2251w, 365.37v
No.2 8.2kwh, 2190w, 365.1v
No.3 8.5kwh, 2333w, 356.47v
No.4 7.2kwh, 2103w, 366.78v
mppt rs
11 comments
And if you switch off one other string to make this one work harder?
Do you hit current limiting at all (200A)
eoin avatar image eoin Alexandra ♦ commented ·
I haven't hit 200amps. I will turn off a string tonight and see what happens tomorrow. Thanks.
eoin avatar image eoin eoin commented ·
On July 30th the battery didnt make it to fully charged so that day all power avaliable should have been used, here are the figures (imput 4 is still down):
No1 4.11kwh 886w 351.56v
No2 4kwh 869w 351.1v
No3 4.15kwh 889w 351.68
No4 3.03kwh 809w 350.73v
The results are in. So this data is from today when the string for imput No.2 was disconnected, battery reached 98% charged so there was allways a draw on power.
No.1 7.39kwh,3539w,245.95v
No.2 0kwh, 0w, 6.11v
No.3 7.39kwh,2697w,350.9v
No.4 6.31kwh, 2344w,240.26v
nesswill avatar image nesswill commented ·
Is string 4 at the exact same angle (might face the same way but the angle to the sun will make a difference) as the other 3 strings?
Can you post the PV Spec's/type please.
eoin avatar image eoin nesswill commented ·
Pannels are rec twin peek 4. 370w, vmpp 34.7v, impp 11.68a, isc 11.38a, voc 41v. 9 pannels per string.
All pannels at 70° pointed south. As I said moving the strings to different imputs on the mppt makes no difference problem stays with imput No.4
nesswill avatar image nesswill eoin commented ·
Ok thank you.
Can you post a graph from VRM showing all 4 strings (i have just posted x2) over the last week please.
Something like this below please...
I only have Internet on my phone and don't own a laptop or pc so I haven't gotten vrm to work properly yet. (I'm off grid as much as I can be).
This is the best I can do screenshot-20230810-084511.jpgscreenshot-20230810-084525.jpg
Thank you.
I guess you have to ask yourself,
Can you live with it?
or
Do you return the unit for testing/repair/replacement? (<<< my option)
Sorry not any more I can add, good luck and please let me know what you decide and the outcome.
Thanks a million, I've a decision to make.
eoin avatar image
eoin answered ·
The power loss is equivalent to 1.29 pannels, I've 36 pannels I think it is an acceptable loss considering the work to fix it. Maby I'm too lazy or too rich.
Very funny accepted answer @Eoin :))
I agree with you, it's a bit weird, but also not enough to worry about.