ee21 avatar image
ee21 asked
Grid Meter to use for Split Phase 240v - 200A Service?
I'm looking for a grid meter for use with Energy Storage System design. I live in the US, with split-phase 240VAC power, my home has 200A service, phase angle is 180*.
Would the Carlo Gavazzi EM24DINAV53DISX work? I wasn't sure since it's marketed as 230VAC 3-Phase compatible which is not available in the US.
ESSEnergy Meter
ee21 avatar image
ee21 answered ·
Got an answer from Carlo Gavazzi support. The EM24 does support Split Phase 240VAC, up to 200A using Current Transformers.
ewbcvec avatar image
ewbcvec answered ·
I am also interested in this question. Did you actually try it?
I'd also ask if ESS accesses the EM24 meter in a manner that results in the total power being read, or if it tries to read the power for each phase and do its own calculations, or something else. Relevant to this:
On this page: https://www.victronenergy.com/live/energy-meters:start?s[]=gavazzi
It says:
In the ET340 - the energy imported and exported is counted at each individual phase and then the Total is provided from the sum of those values.
In the EM24 - the energy imported and exported is counted as a total power, with net differential readings from each phase cancelling each other out.
I'm just guessing that there is no code in ESS specifically for the US split-phase system because it isn't seen in any supported country. So, will it "just work" or are there going to be issues, even if the meter supports it?
11 comments
ee21 avatar image ee21 commented ·
I have not yet, the quote I got from the manufacturer was around 750$ just for the energy meter. I certainly will let you know once I have.
Mike Stasko avatar image Mike Stasko ee21 commented ·
I would also be interested in this solution although the price seems steep for the functionality. Was the $750 retail or are you able to find it cheaper?
Thanks
ee21 avatar image ee21 Mike Stasko commented ·
That was the quote directly from the manufacturer's sales team. And yes, that seemed quite steep indeed, considering the two MultiPlus Compact 2000s I'm using were around $1000 each.
The specific model their sales team confirmed would work with my setup was:
EM24DIN AV5 3D IS X
I was originally concerned because the voltage listed in the specs for this model was misleading (I think it listed something like 230v per phase or something), but that was apparently was a range of acceptable voltages, and the listed value was the "maximum allowed voltage allowed up to" voltage, meaning 120VAC (or split phase 240VAC) would be just fine.
To be honest, at this point in my setup, I have the ESS Assistant working exactly the way I want it to, without the use of an Energy Metering device configured in my Venus GX. I am interested in my whole home's net consumption, but the cost to get that data seems too high at this time, I'd rather spend that money on additional lithium battery modules, but will post here if I ever have extra cash burning a hole in my pocket and do end up buying one.
So today I measure my overall usage through this device: https://iotawatt.com/
At the time I paid $150 for the base station and then spent another $30 or so on some addition CT sensors. From there I graph the data in EMONCMS. I can get a nice view of consumption (GRID & Loads) and production (PV). Biggest thing that is missing for me is Battery Bank SOC / Volts. There are options to grab and graph that data but I have just not got around to buying the addition hardware.
I wonder if there are other CT / meters options that are more economical that are supported by Victron? I did notice that the MultiPlusII leverages a CT clamp I believe similar to what I use for my Iotawatt unit and those can be had for 'cheap'.
I am interested in your overall setup since today I am using a 'cheap' inverter and am looking to upgrade to either Victron or an Outback. Do you have a hybrid setup or completely off grid? I am looking at a hybrid setup to minimize grid usage and avoid selling back. Thanks
I have mostly given up measuring overall net usage, and just taking to inferring based on the data that is available to me/looking at my utility bill. I had an Aeon Labs Home Energy Meter before for about the same price you mentioned, problem with most energy meters besides the Carlos Gavazii ones is they don't read reverse current properly so it became depreciated as soon as I got solar. If you look at the Victron forms, other people have asked the same question and been told no, CG meters are only ones supported besides the Victron branded external CTs.
I have an on-grid connected ESS setup, I use my batteries to offset the energy I use during peak pricing times, to the super-off peak hours. I permit the system to feed in AC back to the grid as well during those hours, as I receive credits that can be used to buy back energy later. What I do to accomplish this is set the Grid Setpoint to -10,000 watts (PV output reaches up to 9,000 watts), and then enable "Limit Inverter Power" so that my battery bank is being discharged at a consistent rate during the on-peak hours; weather that energy goes to my loads, or gets sent back to the grid it really doesn't matter to me. To stop the system from discharging or charging during the "mid-peak" I simply set an option during those hours in "Scheduled Charging", but set the SOC limit low, around 25%, it will charge up to the amount, but not discharge at all during that time. And then during super off-peak, I set it to scheduled charging but with the SOC limit at 100%.
Specifically I have split-phase 240VAC power (Southern California, USA), L1+GND= 120v, L2+GND=120v, L1+L2=240VAC. I have two MultiPlus Compact 24/2000, running in a 180* Split Phase operation mode, with the grid connected on the only AC input. My PV inverter unfortunately is connected in parallel with the grid, NOT on the AC Out of my MultiPlus.. Although the PV inverter is still added to my Venus GX, and is sending the data to VRM. The AC Out of the MultiPlus system goes to a sub-panel which powers my critical loads.
ewbcvec avatar image ewbcvec Mike Stasko commented ·
Yes, I'd also love to learn more about any ESS system running in the USA.
AFAIK: Victron has certified only two 120V Multiplus versions to UL 1741 for the US:
https://www.victronenergy.com/upload/documents/Certificate-of-Compliance,-UL-1741-and-CSA-C22.2,-MultiPlus-12-3000-120-50-120V-&-MultiPlus-24-3000-70-50-120V.pdf
Seems like you need that certification for ESS? I'm hoping for 48V Quattros ... someday.
It would be pretty cool if OpenEnergyMonitor could be used instead of proprietary meters from CG. I'm looking into their integration with openEVSE vehicle chargers already. Charging your car when there is PV available isn't so different from what ESS does is it?
Mike, thanks for the link to iotawatt. I've been looking for a more affordable (& accurate) energy meter. Maybe this is it.
ee21 avatar image ee21 ewbcvec commented ·
Well that's the thing, they really aren't certified yet to my knowledge at least; I didn't even think those two models you referenced were either, maybe I'm wrong though. I contacted Victron support whom informed me from a hardware perspective the current 120VAC line of the MultiPlus's sold in the US should meet all current code requirements, that it was simply a matter of obtaining certification, and then releasing a firmware update.
In the meantime however, and I will preface this by stating the fact that I am not a certified electrician, or Victron equipment installer, or anything in between.. I am an avid DIY-er, and have taken a bit of a gamble I will admit to say the least, by attempting a fully DIY ESS installation, going as far as to use my own homemade 7S lithium battery bank using 18650 cells... This, by current standards here, is not code complaint to my knowledge, however the system is still working beautifully.
Before even attempting a DIY ESS installation, I did at least obtain a "Generating Facility Interconnection Agreement", meaning the utility company was made aware that we planned to install a residential energy storage system that would be selling back energy over the grid mains, something which is actually highly, highly encouraged, and incentivized here in California. Furthermore I looked into anti-islanding, and my PV inverter had not been installed (by a local certified professional) with any additional equipment in this regard, with the exception of the PV inverter's inbuilt protections, which after researching, were on par with the MultiPlus.
The inverters were installed and wired, and configured myself. Having no prior experience with Victron equipment, this was actually a breeze, and I foresee myself being a strict brand loyalist moving forward now, I absolutely love everything about the equipment.
As far as the configuration goes to achieve ESS working in the US, I simply used the "other, not compliant to any local grid code" option, and customized the AC low/high disconnect/reconnect values to be very tight, disconnecting when voltage dropped below 114VAC from 120VAC, or above 125VAC. During my testing of a simulated grid-failure, the MultiPlus's responded in milliseconds when the AC-In was disrupted, severing their connection with the grid, and entering inverter-only operation mode; the voltage across the mains terminals when this occurred dropped to 0V faster than it took me to glance over at my equipment.
@ewbcvec I believe Victron already has some support via the VE.Bus functionality for their MPPT controllers in being able to share Charging/Volts/SOC/etc with Openenergymonitor movement: https://community.openenergymonitor.org/t/integration-with-victron-platform/10867
Something on my todo list to explore.
@ee21 I am looking to do a similar setup but with no grid feedback, selling back to the grid is not advantageous and if anything they just started instituting a monthly 'convenience' fee for selling at a reduced rate back to the electric co.. no thank you.
After reviewing the documentation that I could fine online I am still fuzzy on the following scenario for split phase. (ironically there seems to be more info on the deprecated Hub 3/4 for split phase setups than ESS)
In order to limit any feedback to the grid I assume I would need an energy meter: ET112 or ET340 (single or 3 phase meters). So with two inverters in parallel (multiplus or quattro - 48/3000). Could I leverage two ET112's, one per phase & inverter? Or could i use one ET340 and just two of the phases but send each phase to a separate inverter? I realize they could not share output across the phases so balancing the load panel would be key.
The other big question is does ESS allow for a hard no feed back setting?
Topology wise it would look something like this but with two inverters & no feedback to grid:
Thanks
If your PV is on the DC bus side of your system, and not parallel with the AC Input of the MultiPlus, then you would not technically need an Energy Meter. The way it would work without an energy meter in your scenario, is you would set Grid Setpoint to 0, or the default +50W, the ESS would use as much solar energy as possibly to power the AC loads on the AC-Output of the Multi, without sending extra AC back over the AC-Input terminal and back to the grid (or other loads not on the AC-Out). The only advantage an Energy Meter would provide in this case, is if you have significant loads that are not connected to the AC-Out of the Multi, in this case you would need an Energy Meter so the ESS can "see" those loads, and then balance them out. Personally, I have too many large loads to even hope my MultiPlus could balance in an actual ESS setup, so a simple consistent discharge during the on-peak tariff hours is what works best for me.
Regarding the meters, I believe you can only designate one "active" Energy Meter in the Control GX, I would advise against getting two ET112s for your purposes unless someone else is able to specifically confirm that works. From my understanding with the Garlos Gavazii tech support, the ET340 would be what you want (for 100A or lower service). If you are going for a split-phase ESS like me, one inverter would connect to L1+N, and the other inverter would connect to L2+N, and you simply would not use L3 on the meter (or it might be re-purposed as the Neutral in that scenario, not sure you'd have to read the manual).
@ee21 Thanks for the info.
Brian Brown avatar image Brian Brown ee21 commented ·
Sorry to revive this old thread. LMK if this is inappropriate since this is my first post to the community. I'm in the USA/CA with a split phase 200A service and want to do something similar using (2) Quattro 48/5000's. My question is if you configure the grid code with "other, not compliant to any local grid code" what is the behavior with loss of mains (LOM)? Does it still open the back-feed relay? Or as @ee21 stated do you need to "customized the AC low/high disconnect/reconnect values"? During a power failure I'd like to manually turn off the mains breaker and allow the inverter to power the loads using the back-feed. Unless there's a product that can effectively do that (cut the 200A service) automatically. My PV is DC only using a Smart Solar MPPT. Thanks!
thorium avatar image
thorium answered ·
Reviving this. I do wish we had an option for ESS compatible grid meter in the USA that wasn’t $750.
ESS can be used in the US by using additional UL verified equipment between it and the grid, and many utilities will do assessments of non UL inverters for additional fees so there are often avenues to hook up non-UL inverters via utility inter connection agreement process.
shaneyake avatar image shaneyake commented ·
You could always install any modbus meter and make it work with ESS in Mode 3.
This isn't that hard to do in Node Red if you run the large firmware on the Cerbo.
https://www.victronenergy.com/live/venus-os:large
2x Smart KWh meter 120V with Modbus
https://www.amazon.com/Smart-Single-Energy-anylizer-Modbus/dp/B07D49N8FH/
https://meters.co.uk/wp-content/uploads/2018/07/EM115-MOD.pdf
1x RS485 to TCP/IP
https://www.amazon.com/gp/product/B07C1TC165/ref=ppx_yo_dt_b_search_asin_title?ie=UTF8&psc=1
You can create a flow that takes in the Meter data and sets the Multiplus setpoint.
I know this is outside the scope for the average person but it is a low cost option.
There will be issues, like the ESS setting Menu won't work and VRM will not include this data. Hopefully we can get this NodeRed feature soon and then this will be a viable option for more people and VRM, ESS will work like normal and you won't have to do Mode 3.
https://github.com/victronenergy/node-red-contrib-victron/issues/82
But I just wanted to let people know that there is a low cost option will just need more setting up. As this would be around $200.
thorium avatar image thorium shaneyake commented ·
Thanks. I thought of doing something similar — using IoTaWatt at around $200, which has an API to pull current power use, then have code that constantly reads that and adjusts grid set point on the Victron side.
But as you noted, this kind of thing is a half solution and gets a way from why I’m using Victron in the first place. The ecosystem... e.g, VRM portal missing data, dashboard view on Venus wouldn’t show the mains usage like with the officially supported meter, etc.
The time spent figuring out the coding, then only having a half measure, means it’s more logical to capitulate and get $700 of Carlo Gavazzi stuff.
shaneyake avatar image shaneyake thorium commented ·
Yeah, hopefully when issue 82 is resolved. We will be able to make a really easy guides on how to do things like use your own meter/ expand the list of meters but will have full Victron integration.
It can be currently done if you create your own D-Bus service but that is way more complicated than clicking a few buttons.
offgridsolutions avatar image
offgridsolutions answered ·
In the UK the EM24-DIN.AV5.3.D.IS.X (£300) would be used with CT clamps (£30 each)
thebelcherman avatar image
thebelcherman answered ·
Very old thread, but as of 2/22/2024 prices for the EM24DINAV53XE1X have dropped dramatically. Unaka, located in Spartanburg, SC as them in stock for $494.00. Mate them up with a pair of Carlo's CTD1X2005AXXX CT's, $55 a pop and you're golden. Desperately needed a Grid Meter to monitor my 2 UL list MultiPlus-II 120V 48/3000/35-50's in a Split Phase configuration. Wanted to hold out for the UL listing of the 5K's but they've been promising that for months and nothing.
I'm in EE her in Florida and we use lots of Carlo Gravazzi equipment at all our substations, they're built like tanks, with failure rates far below anything other manufacture. I think at the $600 price-point, they are money well spent.
Just placed my order, let you know how it goes.