Haydn Saunder avatar image
Haydn Saunder asked
Maximum sets of three 15KVA MP2 in a three phase system?
I've seen the datasheet which says "up to 6 sets of three units can be parallel connected for a 75 kW / 90 kVA inverter and more than 1200 Amps charging capacity." but this obviously isn't specs for the 15kva.
Ideally, I'm looking to get more than the 180KVA of power possible with Quattro's for industrial off grid sites.
Any help would be appreciated!
3 phase
snoobler avatar image
snoobler answered ·
From the datasheet:
90kVA/18 = 5kVA units only.
and
1 EA leg can be in a 3 phase system for 8, 10 and 15K models, for 24kVA, 30kVA and 45kVA power but they can't be in parallel on each leg.
https://www.victronenergy.com/live/ve.bus:manual_parallel_and_three_phase_systems
The maximum system size is a 180kVA with 12x 15kVA Quattro, 4 on each phase.
As the datasheet says the MP-II 8kVA and bigger currently can't be configured in parallel, so you have to use the "old" Quattro.