matt1309 avatar image
matt1309 asked
Voltage limit on MPPT
Hi Folks,
I'm looking to understand the MPPT max voltage limit a bit more, for example the 250/100 MPPT.
Max voltage being 250v. Say I have panels with VoC of 49.5, and put 5 in series. (Awfully close to 250v)
VoC is technically under 250v however in practice, in the scenario cloud -> sun with battery disconnected for whatever reason I suspect 250v would be breached even if for a short period of time.
Is the 250v limit on MPPT based on VoC (ie likely has a buffer for the niche scenario described above), or is 250v a hard limit and installers/system designer should add a buffer themselves to ensure the 250v is never breached or is VoC * number in string sufficient.
Thanks,
Matt.
MPPT Controllersvoltageovervoltage
Michelle Konzack avatar image
Michelle Konzack answered ·
It is a hard limit.
Please use the Victron MPPT Calculator because with your 5 Solarpanels you can reach easyly 275V if the temperature drop to -20°C and 290V at -40° if you live in Estonia or similar
matt1309 avatar image matt1309 commented ·
Thank you. Was more looking for understanding that needing a calculator but thank you you've answered it.
MPPT Product Page
MPPT Error codes