I am putting together a dual phase system using 2x 48/10000 Multiplus II for a client who is supplied 3 phase from grid, but only uses 2 of the phases. When commissioning, what phase angle would be required?
I am putting together a dual phase system using 2x 48/10000 Multiplus II for a client who is supplied 3 phase from grid, but only uses 2 of the phases. When commissioning, what phase angle would be required?
It could be 120 or 240 depending on which phases feed which Multi. and their phase relationship. You might check the phases with an oscilloscope.
Parallel, split- and three phase VE.Bus systems manual
Theory on wiring large systems PDF
Three-phase and parallel system theory training presentation
Three-phase & Parallel installation training video
Parallel, split- and three phase VE.Bus systems manual
Theory on wiring large systems PDF
Three-phase and parallel system theory training presentation
Three-phase & Parallel installation training video
Additional resources still need to be added for this topic
36 People are following this question.