question

kw4np avatar image
kw4np asked

Cerbo GX starting generator although SOC is above threshold

The Cerbo GX is repeatedly starting the generator with the reason given as "Low SOC" although the SOC is not lower than the start threshold and the grid is connected. After the minimum run time the generator shuts off to restart again. The SOC generator start threshold is set at 40% and it should recharge to 96%. To resolve the issue I finally turned off autostart.

1672998598652.png

This has happened before on another system and both times the generator was manually shut down the day before the event. It almost seems like the generator is try to recharge to 96% although the system is no longer below the threshold, although it's not clear why this happens hours after the manual shutdown. Is this a known bug?

This behaviour generates lots of errors as because the grid is connected, the generator is not detected. Needless to say, the user doesn't understand what is going on.

cerbo gxVenus OS
1672998598652.png (40.2 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
derrick thomas avatar image
derrick thomas answered ·

Have you tried rebooting the cerbo?

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kw4np avatar image kw4np commented ·
Hi Derrick, I shouldn't have to reboot the Cerbo, but that did solve the issue. It seems the issue is caused when the power comes back on before the battery is charged to the threshold. If the power goes out even momentarily, the generator tries to recharge to the threshold again even though this may no longer be needed or desirable.
0 Likes 0 ·