hastings avatar image
hastings asked
Temperature compensation settin
I am having difficulty interpreting the user manual temperature compensation settings for my Rolls S12 AGM battery bank: 8x 12V batteries (divided into 2x 48V banks). They are charged (solar and generator only) via an EasySolar which is connected to a battery temp sensor.
The manual states:
Am I right to understand that the table above is for use in a setup that needs to be adjusted manually according to fluctuations in the battery temperature?
So I think I should be going by the "NOTE:..." paragraph and the text in bold rather than the highlighted column in the table.
I do not know the number of "cells" I have and should use in the 4mV/C/Cell calculation.
In Victron Connect the setting I am using (a Victron Gel preset) is currently -64.80mV per C. This is for the whole battery bank. Do I alter this to -96mV for the Rolls?
Very grateful for any help.
klim8skeptic avatar image
klim8skeptic answered ·
If you have a 48v battery, yes. Don't forget the minus symbol when entering the value in.
The pink highlighted column also gives Rolls' recommended Bulk-Absorb and Float setpoints for your charger.