marc-jackson avatar image
marc-jackson asked
Autotransformer for Boat application - not getting correct L1/L2 voltage
I have a USA boat with 2 line 120V/230V and now the boat is in Australia.
I fitted a autotransformer so I can input 240v to convert to 2 x 120v .
I have attached the drawing my wiring.
The problem is on shore power I'm getting 240V on line 1 (should be 120V) and getting 120V on the white neutral wire (should be 0V) and the red, L2 0 volts (should be 120V) between the ground bus bar and the same reading between the white bus bar.
If I turn the generator on the system operates normally. all the voltage reading are below.
This wiring is uncommon and I have to wait over 3 months for a technician just to come have a look, so hoping someone might have the answers for me.
I found the problem after my Freezer stopped working, its 120V and with a multi meter had 240V on line 1 and 120V on the neutral.
Shore Power.pdf
Autotransformer
shore-power.pdf (128.6 KiB)
It is probably best to look at the schematics on the product page.
Mike Dorsett avatar image
Mike Dorsett answered ·
AU / Shore power will be 240V on active, ~ 0V on Neutral measured with respect to ground. After the auto transformer, you will have :
L1/G 240V, L1 / N 120V, L1/L2 240V
N/G 120V, N/L1 120V, N/L2 120V
L2/G ~0v, L2/N 120V, L2/L1 240V
If you want to get back to 120/0/120 you will also need an Isolating transformer - in AU standards, the N terminal is grounded at the distribution box, rather than American standard of 120/0/120 having 2 active lines and a centre ground. On a boat you ought to have an isolating transformer in any case, to prevent galvanic corrosion.
marc-jackson avatar image marc-jackson commented ·
Thanks Mike, I'll follow up and add a isolation transformer and let you know the results.