busta999 avatar image
busta999 asked
Is it usual for batteries to drop 20% in 2 mins?
I have 20kWh Lion batteries on a Multiplus II 5kva 48v Every night at the start of cheap rate the batteries start charging they jump from 35% SOC to 55% SOC after 2 mins of charge. Then the moment charging stops they drop from 100% to 80% immediately. This system has been in for only 1 month, but it just seems very odd. Is this normal or to be expected? any ideas on what is going on? Much appreciated.
Multiplus-IIBMS
4 comments
We need more information about your System.
What components do you have? What batteries? Settings? Wiring?
busta999 avatar image busta999 Matthias Lange - DE ♦ commented ·
New to all of this so apologies if doing something wrong.
MultiPlus-II 48/5000/70-50 230V
Leoch - 48-100TCAN Lithium (LiFePO4) Pack - (51.2V/100Ah/5.12kWh)
Victron Cerbo GX - Control & Monitoring Hub Victron GX Touch 70 - Control & Monitoring screen
Victron Lynx Distributor - Modular Fused Busbar (Inc. fuses)
Victron Lynx Power In - Modular Busbar Victron VE.Bus Comms Cable 1,8 m VE.Can to CAN-bus BMS type A Cable 5 m RS485 to USB interface 5m
25mm Black Battery cable
70mm Black Battery Cable
Battery Isolator 300A
What additional config do you require, the Victron is set to Auto for BMS and it is using the Leoch BMS.
Looking the displays for each of the 4 5kWh batteries you can see three have an SOC of say ~ 72% +/- 2% and one, the top one is showing an SOC of ~53%.
busta999 avatar image busta999 busta999 commented ·
Pretty sure I have figured it out.
The first battery, the master, is defective and has lost 20% of its total capacity. So will get it it replaced under warranty.
Thanks
2 Likes 2 ·
stef123 avatar image stef123 busta999 commented ·
Hi Busta, I'm thinking of getting these Leoch batteries, I see you had an issue, is this all sorted now? Would you recommend? Could you share a picture of your set up as sounds very similar to what I'm planning?