question

cesar avatar image
cesar asked

Multiplus 500 remote control

I would like to enable/disable charging and inverter function of Multiplus 500, triggered by external software. What is the recommended procedure to do that?

I was trying to control through d-bus command. I is possible?

Thanks for your kind support.


MultiPlus Quattro Inverter Chargerd-bus
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Mike Dorsett avatar image
Mike Dorsett answered ·

this can be done with hex commands to the Mk2 (or Mk3), also you could load the 2 wire bms assistant into the multi and use the aux inputs to control this remotely. Depends on how the rest of the system is configured. d-bus commands would possibly work through a Venus os device, by setting max charge and discharge limits.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.