question

merav avatar image
merav asked

Easysolar not diconnecting my system when the batteris are low.

My solar system is EasySolar24/1600 and BMV-700.
However, last week the batteries went down to %0 (because the solar panels got disconnected by accident for 2 days).
My understanding was that the Easy Solar need to disconnect the system at factory setting to protect the batteries from ever going down to %0.
Any thoughts on what is wrong here ?
Thank you very much

merav

EasySolar All-in-One
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
klim8skeptic avatar image
klim8skeptic answered ·

What values have you programmed the Multiplus regarding low battery shutdown?

multi-low-batt-shutdown.png

Note, the Soc in the above shot refers to the multiplus's calculated Soc, not the BMV readings.


1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

@merav also the easysolar cannot control DC loads

0 Likes 0 ·
merav avatar image
merav answered ·

The unit was programed by a friend, who is not available to contact now.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Unless you can find someone else to help, you must monitor manually. But also look at loads connected direct to the battery.
0 Likes 0 ·