Willem avatar image
Willem asked
Why does Quattro 8000 1-ph not allow full charging current from generator
Installation: Quattro 8000 / 6xpylontech 48V batteries / generator 12kVA VAR / 6000W 48V PV
CCL set at 222A
Why does the Quattro limit the generator charge duty of batteries to total of 3800W (13A/battery) if batteries can take 40A continuously?
During generator charging, Quattro directs 3800W to batteries and e.g. additional 3000W to end users.
battery charging
Alexandra avatar image
Alexandra answered ·
@Willemao
What is your input current limit? Do you have other loads on as well?
Is weak AC checked? Alternatively the charge current from grid is set that low.
JohnC avatar image
JohnC answered ·
Hi @Willemao
Your Quattro has a rated charge limit of 110A, and by default it is probably set lower than that. Have you had a look?
Willem avatar image
Willem answered ·
Have resolved the problem. She charges at 110A now.
Thanks for the help.
It would be good to know what the problem was, if others run into the same issue.