VictronMultiPlus-II 48/5000/70-50 Generator to Charge the Battery

I have a Victron MultiPlus-II 48/5000/70-50 5kva system , I want to put a silent inverter generator as backup. What type of Generator do I need to get to charge the battery Lithium Ion 3.5KWh Pylon US3000 in extended period of power outage. What is approved to use on this system

Generatorcharging battery
10 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Paul B avatar image

There are really no approved generators that I know of,

so a good quality unit is what I would suggest or test and make sure it works befor you buy if you can.

To cover ease of use I would suggest a 5 to 7 Kw generator as this can charge the batteries and also run the loads as well

This is presuming that the Inverter is size correctly for the loads that its needed to run in a blackout.