Hello folks,
Working on install with Victron Lithium Smart 330A battery to a Lynx distributor system. Question on fusing. I am trying to find out if Victron publishes the short-circuit current rating so I can validate that the MEGA fuse in the Lynx distributor has a high enough AIC for the battery OR whether I need to go to an external class T fuss with a higher AIC.
This is separate from fusing to meet the minimum requirement of protecting the battery cable and more in understanding the AIC rating I need to have.
Lithium Battery
wkirby avatar image
wkirby answered ·
Cells of this size are typically down to 0.1mΩ depending upon SOC of course. So 0.4mΩ per battery.
Excluding cables, fuses and the component at fault, that would be 32kA.