pieter avatar image
pieter asked
MultiPlus 12/1600/70-16 230V Not Starting When Powered Up
Newly installed MultiPlus 12/1600/70-16 230V enters alarm when powered up. 230Volt AC-In connected and 2 x GEL 110Ah connected in parallel (12Volts)
When MultiPlus is switched on the inverter comes on, fan runs for about 2 sec then switches off and alarm LED is ON.
Trouble Shooting Table just says "Check the table for the appropriate course of action)
Where I purchased the MultiPlus, they don't know either!
error
Paul B avatar image
Paul B answered ·
More information is needed.
IE when you turn the multi on whats that voltage at the battery terminals.
and whats the voltage at the inverter input terminals
And I mean just as it turns on and before the error
pieter avatar image pieter commented ·
Thank you for your response. I did not check the voltage during start-up. I have send the unit back for checks at supplier. Why do you ask this? Could the batteries voltage be too low? The batteries are new Victron Gel batteries. As is the batteries measure 12.66vdc