Multiplus II 5kVA 48V random output voltage dips

I fairly recently installed a Multiplus II 5kVa 48 system (including Venus GX), connected to 2 x Hubble AM-2 5.5kHw lithium batteries. System runs as purely backup system for load shedding purposes.

This issue that has arisen is that the inverter randomly cuts the output voltage to the loads for a couple of second.

The latest instance happened after a blackout (load shedding). The system took

over and returned seamlessly, and roughly a hour after, the output voltage dipped for a couple of seconds.


-Inverter and GX has latest firmware installed

-System is not overloaded

-AES is not enabled

-Battery bank is CAN bus connected to the GX, via its own logging device (Cloudlink\Riot)

I have checked settings multiple times, and compared to other installations.


Has anybody had similar problem, or have advice as to remedy?

Thanks


voltage-in-and-out.jpg

Multiplus-IIbatteryvoltage
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
botessj avatar image
botessj answered ·

As a sidenote. This does not only happen after loadshedding

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

marekp avatar image
marekp answered ·

@botessj@gmail.com

I do not have the answer for your question but I had similar occurrence but my system showed an error #1 device switched of.

problem.jpg


problem.jpg (175.7 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

nickdb avatar image
nickdb answered ·

There was another member here a while back with hubble issues.

They have not been tested with Victron and are not on the compatibility list.

From that post (you can search for it), it sounds like they can't provide proper settings for victron and may have BMS issues.

Suggest you contact them for support.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.